What is the maximum number of breaker spaces allowed in a residential panel box. Article #?
The reason that your article got lost is that the NEC "lost" it too. Not sure what year that happened.What is the maximum number of breaker spaces allowed in a residential panel box. Article #?
I guess on 2008.The reason that your article got lost is that the NEC "lost" it too. Not sure what year that happened.
I have installed 84 space NQOB panels. I think the most circuits they offer in the "Loadcenters" is 60 spaces.It used to be 42 but not anymore.
I think Sq-D maked a 62 or 72 space panel.
That is a 40 space panel that is designed to accept tandems in every space giving you 80 circuits.Square D Homeline 40-space, 80-circuit
http://www.homedepot.com/p/Square-D...ug-on-Neutral-Ready-HOM4080M200PCVP/204836379
Yes. That's why I wrote 40-space, 80-circuit.. split bus all the way down, fill it up with non-circuit-limiting tandems, quads, whatever you want.That is a 40 space panel that is designed to accept tandems in every space giving you 80 circuits.
Are you still using Zinsco and Sylvania panels? LOLA 80 space panel with 1 inch wide breakers is going to be 80 inches tall just for the portion where branch breakers are located, add a 200 main breaker on one end and the usual few inches on opposing end and you have a cabinet around 8 feet tall Plus it is pretty much impossible to comply with 404.8(A) with all switch handles.
Too early in the morning to think correctlyYes. That's why I wrote 40-space, 80-circuit.. split bus all the way down, fill it up with non-circuit-limiting tandems, quads, whatever you want.
Are you still using Zinsco and Sylvania panels? LOL
last I knew, every panel made now has two rows of breakers. That Homeline bus is only 20 spaces tall. A true 80 space bus would only be 40 spaces tall.
Too early in the morning to think correctly
You are right would only be 40 spaces tall. I guess I had a couple recent panels I have installed clouding my mind that were in ~80 inch tall cabinets, one a 84 space NQ and another 66 space NF - but they each had 400 amp main breakers as well:slaphead:
Correction to my earlier post concerning non-circuit-limiting tandem breakers (for usewhen the bus isn't split).
With split bus, that Homeline panel can be filled up with circuit-limiting breakers (the ones with the little guard in the stab slot)
Finally got some coffee, my thinking is better now
What is the maximum number of breaker spaces allowed in a residential panel box. Article #?
Yeah, I think the proper terminology would be notched bus instead of split bus. I've seen the old two section panels, where the lower section was fed with jumper wiresThough I know what you are talking about, some may think of the old two bus section panels that were commonly called split bus, they had main lugs spaces for up to six double poles, with one of them being the "lighting main" and it supplied the second bus, which typically had more spaces then the "mains" bus.
I'm not sure if Square D makes a non-ctl tandem for Homeline, just an assumption on my part. I know it has an extra nub at the base of the bus, and the breakers have an indent on the bottom to account for it.. that makes it almost impossible to find other brands that will slide in all the way.Does Square D even make a tandem breaker for the Homeline series that doesn't have rejection features if the panel wasn't intended to use tandems in certain positions? Homeline series is not old enough to have been around before they required this rejection feature and non-ctl breakers for other panels are intended for replacement use only.
Saw one on display at the supply house, asked the counter guy about them and he said all they are making now is panels that can accept plug on neutrals.Just installed a Homeline panel yesterday that I previously didn't know was availabe - 42 spaces that can accept tandems in all 42, and had plug on neutral bus as well. I also didn't know they made the plug on neutral in the Homeline series.
They have all that worked out, spacing for the screws on the neutral buss is staggered.Haven't seen the plug on neutral breakers yet, we will see how those work out later on. Looks like you need to watch where you land neutrals, EGC's if a service panel, though as when you install AFCI/GFCI's you will not have access to any behind those breakers without removing those breakers
Just the Homeline? I have been getting QO panels that are same as they have always been lately - but I haven't been doing much residential work so no need for AFCI's. I still don't like the Homeline neutral location or other competitors with similar arrangement - not so bad for first time connections when things are new, but a PIA to get to neutrals later when breakers are installed with conductors landed on them.Saw one on display at the supply house, asked the counter guy about them and he said all they are making now is panels that can accept plug on neutrals.
They have all that worked out, spacing for the screws on the neutral buss is staggered.