Hello all, I lost the 'c' phase off the load side of a 120/208 transformer. Come to find out, I had a direct short (ungrounded conductor to equipment) that didn't trip the breaker. I located the problem (neutral not bonded at xfrmr) but am wondering why the xfrmr shut down the 'c' phase (which was the phase that the short was on) and my a & b phases were reading 208 to ground instead of 120. any ideas?