hi where is the breaker down sizing rule thanks
george lohri said:hi where is the breaker down sizing rule thanks
Dennis Alwon said:You can often downsize a breaker as long as the load is not greater than the breaker capacity. More often one can upsize a breaker---
Article 240.4(B). It is really about upsizing the breaker but gives the rules for when you can. Thus it will tell you when you cannot upsize.
Art. 240.4(C) says if the OCP is over 800 amps you cannot upsize at all.
Pierre C Belarge said:I would bet all of Dennis's money that the section number that Dennis posted is what the OP is referencing.