I have a project in which there is a dispute brewing among those of us working on it. I am the integrator, someone else has the installation contract.
10 identical machines in a room, hard wired (as opposed to plug-in). Each one has a 480V motor and a 480V 1 phase heater in it, plus various and sundry sensor circuits. Because of the heat, all of the controls for each machine go to a central control panel just outside the door of this room, housing the motor starters, breakers, contactors for the heaters, PLC, HMI and power supply. I designed in a Main Fusible Disconnect with a flange mount handle (to meet NFPA79 just in case). That is the only disconnect accessible from the outside of the box. Each motor starter and heater circuit has it's own breaker, but they are not going through the enclosure door.
The issue in dispute is over LOTO disconnects for each machine. The electrician installing it seems to believe that each motor and each heater in each machine must have a separate local LOTO disconnect, because they are not "within sight" of the control panel that has the lockable main disconnect.
My viewpoint is this; if the owner accepts that when someone wants to work on one machine ALL 10 WILL HAVE TO BE LOCKED OFF, then procedurally, having the one LOTO disconnect on the main is OK as long as he also labels each machine properly (proper label wording is another sub-issue I'll need to address).
Normally I wouldn't sweat it and just go along with the disconnects, we all know that's the safest way. But the big bone of contention here is that there are over 100 machines in the project, so 2 additional LOTO disconnects on each machine, no matter how cheaply I can get them, are going to amount to a big installed cost item and since it is already way over budget it is potentially a project killer!
The idea of using the breakers in the control panel has come up, but having 20 through-the-door rotary disconnect handles is extremely unpleasant to me. I've been the poor schmuck who has had to try to get a bunch of handles like that all lined up to close the door, I wouldn't wish that (or design that) on anyone. LOTO clips for the breakers inside the box was another option offered up, but I contend that Arc Flash rules now make that very impractical, if not impossible to implement; someone would have to don the PPE "bunny suit" just to install and then again remove any padlock and we all know THAT is not going to happen a second time.
Thoughts?
10 identical machines in a room, hard wired (as opposed to plug-in). Each one has a 480V motor and a 480V 1 phase heater in it, plus various and sundry sensor circuits. Because of the heat, all of the controls for each machine go to a central control panel just outside the door of this room, housing the motor starters, breakers, contactors for the heaters, PLC, HMI and power supply. I designed in a Main Fusible Disconnect with a flange mount handle (to meet NFPA79 just in case). That is the only disconnect accessible from the outside of the box. Each motor starter and heater circuit has it's own breaker, but they are not going through the enclosure door.
The issue in dispute is over LOTO disconnects for each machine. The electrician installing it seems to believe that each motor and each heater in each machine must have a separate local LOTO disconnect, because they are not "within sight" of the control panel that has the lockable main disconnect.
My viewpoint is this; if the owner accepts that when someone wants to work on one machine ALL 10 WILL HAVE TO BE LOCKED OFF, then procedurally, having the one LOTO disconnect on the main is OK as long as he also labels each machine properly (proper label wording is another sub-issue I'll need to address).
Normally I wouldn't sweat it and just go along with the disconnects, we all know that's the safest way. But the big bone of contention here is that there are over 100 machines in the project, so 2 additional LOTO disconnects on each machine, no matter how cheaply I can get them, are going to amount to a big installed cost item and since it is already way over budget it is potentially a project killer!
The idea of using the breakers in the control panel has come up, but having 20 through-the-door rotary disconnect handles is extremely unpleasant to me. I've been the poor schmuck who has had to try to get a bunch of handles like that all lined up to close the door, I wouldn't wish that (or design that) on anyone. LOTO clips for the breakers inside the box was another option offered up, but I contend that Arc Flash rules now make that very impractical, if not impossible to implement; someone would have to don the PPE "bunny suit" just to install and then again remove any padlock and we all know THAT is not going to happen a second time.
Thoughts?