I have 67 12/2 MC cables to land in two large panels. I would like to have it look neat.
My idea as of now is to run some strut horizontally and use 1" strut straps. It looks like 6 MC cables will comfortably fit in a strap.
I was concerned about " bundling " and not passing a rough in inspection.
As I understand it though you can put 10 MC cables together before bundling is a concern?
Any clarification would be much appreciated.
here is the code section i was looking at:
310.15(B)(4) Adjustment factors shall not apply to Type AC
cable or to Type MC cable under the following conditions:
a. The cables do not have an overall outer jacket.
b. Each cable has not more than three current-carrying
conductors.
c. The conductors are 12 AWG copper.
d. Not more than 20 current-carrying conductors are in-
stalled without maintaining spacing, are stacked, or are
supported on?bridle rings.?
(5) An adjustment factor of 60 percent shall be applied
to Type AC cable or Type MC cable under the following
conditions:
a. The cables do not have an overall outer jacket.
b. The number of current carrying conductors exceeds 20.
c. The cables are stacked or bundled longer that 600 mm
(24 in) without spacing being maintained
My idea as of now is to run some strut horizontally and use 1" strut straps. It looks like 6 MC cables will comfortably fit in a strap.
I was concerned about " bundling " and not passing a rough in inspection.
As I understand it though you can put 10 MC cables together before bundling is a concern?
Any clarification would be much appreciated.
here is the code section i was looking at:
310.15(B)(4) Adjustment factors shall not apply to Type AC
cable or to Type MC cable under the following conditions:
a. The cables do not have an overall outer jacket.
b. Each cable has not more than three current-carrying
conductors.
c. The conductors are 12 AWG copper.
d. Not more than 20 current-carrying conductors are in-
stalled without maintaining spacing, are stacked, or are
supported on?bridle rings.?
(5) An adjustment factor of 60 percent shall be applied
to Type AC cable or Type MC cable under the following
conditions:
a. The cables do not have an overall outer jacket.
b. The number of current carrying conductors exceeds 20.
c. The cables are stacked or bundled longer that 600 mm
(24 in) without spacing being maintained