ceb58
Senior Member
- Location
- Raeford, NC
Went on a call today to a rental house today that is owned by a good customer. Had some circuits just going stupid like it was a loose neutral. When the circuits started acting up on Fri. night the guy renting the house had enough sense to just kill the main until I could get there. Traced them out into the attic. Squirrels had gotten in through an abandon vent line and had been chewing on some wires in an open j-box. Fix every thing put a cover on and sealed the vent. Things still acted like a loose neutral. Looked at the over head triplex and it "looked good" no bad crimps. Pull meter check connections, check main breaker and neutral bar. Crawl under house to look at the SE cable from meter to MDP. Nothing eaten up. During this time there was some strong wind gust and some small limbs that were touching the triplex knocked the neutral wire off the triplex about four feet out from weather head. Call poco, they come and replace the triplex every thing was good. The squirrels had chewed the neutral and it looked like there was only one strand holding. The one strand had melted in to and just the wrap of the wires was holding it in place until the wind and limbs knocked it off. The only thing we found damaged in the house was the washer and dryer. They are the front loading type with the electronic boards. I think they took a hit from the over voltage. Left the two chewed ends with the renter if he needed to file a claim with insurance.