It is important to understand power limited and non-power limited circuits....As you reference Article 760 I assume your question is regarding the installation of fire alarm and power circuits.
I do not have the 2005 Edition, but 2002 Edition,Section 760.55 states:
Separation from Electric Light, Power, Class 1, NPLFA, and Medium Power Network-Powered Broadband Communications Circuit Conductors.
(A) General. Power-limited fire alarm circuit cables and conductors shall not be placed in any cable, cable tray, compartment, enclosure, manhole, outlet box, device box, raceway, or similar fitting with conductors of electric light, power, Class 1, non?power-limited fire alarm circuits, and medium power network-powered broadband communications circuits unless permitted by 760.55(B) through (G).
The intent of this section is to prevent a a technician from working on low and high voltage circuits in the same raceway.