Customer with relabeled VFDs on vacuum pumps that trip often enough with an Earth Fault code. The Dairy tech usually works on these until he is stumped. We went up and megged the motor & the VFD load side conductors. No faults. The tech always says its the POCO giving bad voltage. OK.
We figured out the drives are ABB and came across the parameter that allows us to disable the GF while the drive is not in operation. Enabled which is the default may cause false positives. We can also set the level of detection. Low for American, Medium for European or HIgh.
What are these levels? 5ma, 30ma, 120ma? (IDK, I just picked #s.)
We figured out the drives are ABB and came across the parameter that allows us to disable the GF while the drive is not in operation. Enabled which is the default may cause false positives. We can also set the level of detection. Low for American, Medium for European or HIgh.
What are these levels? 5ma, 30ma, 120ma? (IDK, I just picked #s.)