Can we install a 200A panelboard with 150A main circuit breaker downstream to a 250A circuit breaker with 250A feeder? The distance is more than 100 feet. If we can or cannot, would you please point me to NEC article? Thank you.
Thanks for your reply. My concern is the panel since it is rated 200A with 150A main circuit breaker. The upstream feeder circuit breaker is 250A. Do you think the panel needs protection from upstream circuit breaker?Yes there is no restriction, as long as the conductors are protected and everything is appropriately sized for the load
Thanks for your reply. My concern is the panel since it is rated 200A with 150A main circuit breaker. The upstream feeder circuit breaker is 250A. Do you think the panel needs protection from upstream circuit breaker?