mshields
Senior Member
- Location
- Boston, MA
If you've got a 112.5kVA transformer with 115deg rise, it has an overload capability of I believe 12%. Therefore it's essentially rated for 126kVA
Assuming you will have primary and secondary protection, the primary may be up to 250% of the FLA, the secondary, up to 125%.
Should those percentages be applied to the FLA associated with 112.5kVA or 126kVA?
It seems to me that in order to use the overload capability, it would need to be the latter. Yet, there is something counterintuitive in doing so, given the nameplate kVA rating of 112.5kVA.
Assuming you will have primary and secondary protection, the primary may be up to 250% of the FLA, the secondary, up to 125%.
Should those percentages be applied to the FLA associated with 112.5kVA or 126kVA?
It seems to me that in order to use the overload capability, it would need to be the latter. Yet, there is something counterintuitive in doing so, given the nameplate kVA rating of 112.5kVA.