Low Temperature Adjustment

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If the ambient temperature is 59° with #3 copper 90C wiring then can I actually load my conductor to 112 amps and use a 125 amp breaker.

#3 at 75C is 100-- 100 * 1.12 (temp correction) = 112 amps or do I have to use the correction at the 90 C and never be over the 75C at 100 amps.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
If the ambient temperature is 59° with #3 copper 90C wiring then can I actually load my conductor to 112 amps and use a 125 amp breaker.

#3 at 75C is 100-- 100 * 1.12 (temp correction) = 112 amps or do I have to use the correction at the 90 C and never be over the 75C at 100 amps.

You can load the #3 to 115 amps and use a 125A breaker (assuming your not using any continuous loads which may require a larger conductor.)
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
That is what I thought but I think you mean 112 amp load. No?

The 75deg correction factor for 59deg F ambient is 1.15.

You could apply the 90deg correction factor to the 90deg ampacity 115A x 1.12= 129A, but I don't believe that 110.14(C)(1)(b)(2) will allow the conductor to be used beyond the 75deg ampacity, which is 115 amps at 59deg F.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
The 75deg correction factor for 59deg F ambient is 1.15.

You could apply the 90deg correction factor to the 90deg ampacity 115A x 1.12= 129A, but I don't believe that 110.14(C)(1)(b)(2) will allow the conductor to be used beyond the 75deg ampacity, which is 115 amps at 59deg F.

I am getting Déjà vu.
 