low volt LED puck lights

Status
Not open for further replies.
I have six cabnets that need LED puck lights. Rather then buying a transformer for every location I ran #18 lamp wire to every location. Did not know if I might find a proublem with voltage drop due to the distance of each run (about 25'). if so can I use another transformer with a higher volts or amps out put? the transformer it comes with is 12v 1a
 
For LED lights the #18 over 25' might not be a problem, but as others have noted, the cable is no good for other reasons.
 
do you think i will have a proublem with the distance of the wire runs?
I agree with Infinity. The LEDs will be around a 100 milliamps, give or take, per puck. And even if a puck is twice that, consider this: 25' of 18 ga stranded copper, puck to transformer, from Table 8 in Chapter 9 of the NEC, will have a total circuit resistance of 1.3 Ohms.

The total voltage drop at the LED will be 0.13 Volts per 100 milliamps.
 
Since the wire is in and there really is no imminent threat, you could "test" it as is. Just so you could evaluate your wire thickness/length for future reference. Then if you don't get around to changing it right away, shame on you.

But 12-14 gauge landscape cord would have been a smarter mistake. If is is showing in the top of the cabinet, then it is OK, and not concealed. Who is going to poke their head inside the cabinet? So if you have to fix it, just run it close to the door up on the front faceframe area.
 