Low Voltage (12VDC - 24VDC) Heat Trace

Status
Not open for further replies.

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
There is heat trace that is rated for classified locations, but I have never seen it at that voltage level. The lowest voltage I have seen is 120.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Is there such thing as finding a low voltage heat trace system particularly in the 12 -24Vdc range that is rate for hazardous locations?

Nope, however there is a mesh system that runs on 50v or so.
 
Ya I have searched all over for such a system and it ceases to exist.. What we are trying to do is use small wind turbines/ solar panels to charge batteries .. Which would be used to control the heat trace.. Thanks for your input
 
Status
Not open for further replies.