Mshields,
hope this helps -
Straight out of the NEC handbook-
Where wire-type grounding conductors are installed in multiple raceways or cables used to enclose conductors in parallel, a full sized equipment grounding conductor selected from table 250.122 based on the size of the OCPD device protecting the paralleled circuit is required in each racewayor cable.
The full sized equipment grounding conductor is required to prevent overloading and possible burnout of the conductor should a ground fault occur along one of the parallel branches. The installation conditions for paralleled conductors prescribed in 310.14 result in proportional distribution of the current-time duty among the the several paralleled conductors downstream of the paralleled set of conductors.
Exibit 250.47 shows a parallel arrangement with two nonmetallic conduits installed underground. For clarity, a one-line diagram with equipment grounding conductors is shown. A grond fault with equipment grounding conductors is shown. A ground fault at the enclosure will cause the equipment grounding conductor it the top conduit to carry more than the proportionate share of fualt current. Note that the fault is fed by two different conductors of the same phase, one from the the left, and one from the right. The shortest aned lowest-impedance path to ground from the supply panelboard is through the equipment grounding conductor in the top conduit. The grounding path from the fault through the bottom conductor is no longer of higher impedance. therefore, the equipment grounding conductor in each raceway must be capable of carrying a major portion of the fault current without burning open.
Straight out of the NEC handbook-
Where wire-type grounding conductors are installed in multiple raceways or cables used to enclose conductors in parallel, a full sized equipment grounding conductor selected from table 250.122 based on the size of the OCPD device protecting the paralleled circuit is required in each racewayor cable.
The full sized equipment grounding conductor is required to prevent overloading and possible burnout of the conductor should a ground fault occur along one of the parallel branches. The installation conditions for paralleled conductors prescribed in 310.14 result in proportional distribution of the current-time duty among the the several paralleled conductors downstream of the paralleled set of conductors.
Exibit 250.47 shows a parallel arrangement with two nonmetallic conduits installed underground. For clarity, a one-line diagram with equipment grounding conductors is shown. A grond fault with equipment grounding conductors is shown. A ground fault at the enclosure will cause the equipment grounding conductor it the top conduit to carry more than the proportionate share of fualt current. Note that the fault is fed by two different conductors of the same phase, one from the the left, and one from the right. The shortest aned lowest-impedance path to ground from the supply panelboard is through the equipment grounding conductor in the top conduit. The grounding path from the fault through the bottom conductor is no longer of higher impedance. therefore, the equipment grounding conductor in each raceway must be capable of carrying a major portion of the fault current without burning open.
[i}The drawing wouldn't transfer...it's two metal boxes with PVC inbetween, parallel raceways stacked. The top one gets a fault at entry of the hub. Demo's large portion of fault current travelling on one equipment grounding conductor. [/i]
This pretty well clears up the expanation as to why thegrounding conductor is upsized in parallel conduits or cables.
This pretty well clears up the expanation as to why the grounding conductor is upsized in parallel conduits or cables.