- Occupation
- engineer
I had a task dropped into my lap. Our company is branching into home automation design. My boss told me to figure out whether our upcoming boxes can be wired properly in NEC/NFPA installations, and how that might look.
I’m an EE by training and practice, quite a bit of it in design of power supplies for things that eventually got their ETL certification. I know that I >don’t< know much about how the NEC/NFPA says to wire things up.
The product is to be a hard-wired logger for conditions in HVAC and plumbing installations that do not already have on-board smarts. Some setups will require connecting to the mains wires on in-place equipment to watch voltage, current, phase, etc. I know what to do with the mains voltage conductors inside our box, but the more I read of how to satisfy NFPA, the more I get confused about exactly how this affects everything all the way back to out box’s power supply.
I’ve followed the chain down to 725.136, probably section (I), but I’m also very aware of my lack of experience.
1. Does the monitoring box have to have a physical barrier inside between Class 1 and Class 2 wiring?
I think no, per 725.136(I), as long as the Class 1 and Class 2 are separated by 6mm or more.
2. If the mains voltage being sensed is connected to a PCB inside the box, and the PCB inside provides ETL-standards of isolation (hi-pot, creepage, clearance, contamination class, etc.), must the power cable entering the box meet Class 2 wiring standards if it’s a permanent installation?
3. Does the power cable have to be Class 2 wired from the AC supply that feeds the power supply? Or Class 1 because Class 1 enters the enclosure?
4. Can the power cable be flexible/stranded? I think no, based on reading the code
Sorry for the long-winded question, and thank you for any pointers to things I’ve missed.
I’m an EE by training and practice, quite a bit of it in design of power supplies for things that eventually got their ETL certification. I know that I >don’t< know much about how the NEC/NFPA says to wire things up.
The product is to be a hard-wired logger for conditions in HVAC and plumbing installations that do not already have on-board smarts. Some setups will require connecting to the mains wires on in-place equipment to watch voltage, current, phase, etc. I know what to do with the mains voltage conductors inside our box, but the more I read of how to satisfy NFPA, the more I get confused about exactly how this affects everything all the way back to out box’s power supply.
I’ve followed the chain down to 725.136, probably section (I), but I’m also very aware of my lack of experience.
1. Does the monitoring box have to have a physical barrier inside between Class 1 and Class 2 wiring?
I think no, per 725.136(I), as long as the Class 1 and Class 2 are separated by 6mm or more.
2. If the mains voltage being sensed is connected to a PCB inside the box, and the PCB inside provides ETL-standards of isolation (hi-pot, creepage, clearance, contamination class, etc.), must the power cable entering the box meet Class 2 wiring standards if it’s a permanent installation?
3. Does the power cable have to be Class 2 wired from the AC supply that feeds the power supply? Or Class 1 because Class 1 enters the enclosure?
4. Can the power cable be flexible/stranded? I think no, based on reading the code
Sorry for the long-winded question, and thank you for any pointers to things I’ve missed.