Low voltage cable in the same conduit?!?
gregory
Re: Low voltage cable in the same conduit?!?
Michael,
Yes, they can be combined in one raceway if they all have insulation for the highest voltage see 620.36 Different Systems in One Raceway or Traveling Cable. for more information. Also you need to shield the wires so that they do not interfere with each other. This is not a code requirement.
[ July 10, 2003, 10:07 PM: Message edited by: gregory ]
tom baker
Bremerton, Washington
Master Electrician
Gregory, although 300.3(C)(1) would seem to allow low voltage and power in the same conduit, there is a FPN that everyone misses referring to 725.54. Please review section 90.3 for the code arrangement. It is assumed when you read the NEC you understand 90.3.
So the answer probably they can be run in the same conduit. You'll also need to review art 800, 810, 820 and 725.
Or get the recently published Mike Holts Understanding Low Voltage and Limited Energy...
tom baker
Master Electrician
Pierre, a point that Mike Holt makes is the code does not define Low Voltage. Its terms are limited energy and class 1, 2, 3 power limited, etc. But low voltage is the industry jargon we all use.
pierre
Tom
Like Romex, BX, and sub panel to name a few, 'Low Voltage' is a common term (slang) to hear. The problem is, different parts of the industry use different voltages as low voltage. Depending on who one talks to, low voltage could be 7140v, 120v, or 12v, just to name a few. I have Mike's new book, and I like it for the same reasons I like his other books. Noel Williams also has written a very good book on 'Limited Energy Systems'.
Articles 411, 504, 640, 720, 725, chapter 8 and other parts of the code are what I call 'lonely' parts.