Low Voltage Cable (less than 100V) Conduit fill

Status
Not open for further replies.

tstollmeyer

New member
Location
California
Does the NEC cover "low voltage" cable?? If so, what are the guide lines to allowable wire fill in a conduit?

[ April 03, 2003, 01:46 PM: Message edited by: tstollmeyer ]
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Low Voltage Cable (less than 100V) Conduit fill

You don't state what type "low voltage", it does make a difference as to the code rules.Its more of a performance issue than a code issue. for example, telecommunications wiring, per art 800, does not have a conduit fill, but the maxium pulling tension is 25 lbs per EIA/TIA standards. Most telcom specs limit you to 180 degrees of bends.
 