Re: low voltage cable (less than24v) and pneumatic tubing in
Originally posted by huston:
Can pneumatic tubing be installed with low voltage wiring in the same raceway as it is an intergral part of a temperature control system. I am being told this violates 300.8 but I disagree on three points:
1. I believe this is referencing 600v cable,
Not only 600 v cable but any wiring covered from Chapters 1 to 7 of the NEC.
Originally posted by huston:
2. this pneumatic tubing in the application above is not an "other" system its the same system and often times goes to the same device and a shared control panel
As far as the NEC is concerned an air supply system is in fact another system from a electrical supply system regardless of them being part of the same machine.
Originally posted by huston:
3. Panels are constructed and shipped all of the world that have DDC signal and pneumatic connections in the same enclosure which is also a raceway.
The construction of those panels are not covered by the NEC.
Originally posted by huston:
I believe that 800.52 should apply to this type installation
It might, is it telephone or telegraph wiring?
If in fact the wires in question are covered by any Section in Chapter 8 of the NEC than 300.8 does not apply at all,
800.1 Scope.
This article covers telephone, telegraph (except radio), outside wiring for fire alarm and burglar alarm, and similar central station systems; and telephone systems not connected to a central station system but using similar types of equipment, methods of installation, and maintenance.
What is the function of the wires you wan to run with the air lines?