Low Voltage Cable run w/ Natural Gas Line

Status
Not open for further replies.

jde75

Member
Location
Burnsville, NC
Hello all,

New to the forum and need a little input: We have a microbrewery under final construction phase here and the owner needs to run some 18/4 low voltage cable to some sensor probes in the brewing vats. Due to the layout of the room he has asked if it is allowable to zip tie the cable to the 1" black iron natural gas piping that runs along the ceiling and down to each vat. I'm trying to help him out with a solution but of course want it to be safe! Thanks in advance...:)
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
The Code prohibits LV (or any other wiring) from being supported by any kind of piping such as you suggest. Nothing to do with NG.If it were me I would run conduit down the walls (probably EMT if not washdown areas) with the LV wiring pulled through it.

-Hal
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
We have some microbrewery setups in this area where some portions of the facility carry a Hazardous Classification. Might be worth checking.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
The Code prohibits LV (or any other wiring) from being supported by any kind of piping such as you suggest. Nothing to do with NG.If it were me I would run conduit down the walls (probably EMT if not washdown areas) with the LV wiring pulled through it.

-Hal

WHERE DOES IT SAY THAT?
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
So I can ty-rap my 6 inch bundle of CAT6's to the sprinkler pipes? :eek:hmy:

300.11(B). By extension, if you can't hang plumbing off conduit you can't hang conduit off plumbing.

-Hal
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
So I can ty-rap my 6 inch bundle of CAT6's to the sprinkler pipes? :eek:hmy:

300.11(B). By extension, if you can't hang plumbing off conduit you can't hang conduit off plumbing.

-Hal

Sprinkler piping, nope, per the sprinkler Codes.
A conduit or raceway, nope, according to 725.143
A gas pipe,,, probably not but I don't think its addressed by the NEC, likely the mechanical Codes.
 

JFletcher

Senior Member
Location
Williamsburg, VA
Welcome!


That's why I said the Code. :angel:

-Hal

and not "the" Code (the NEC).

OP, what you propose is likely against mechanical code(s), tho I have lost count of the amount of thermostat wiring to HVAC units zip tied to natural gas piping Ive seen. If it's considered related equipment, there is a long shot it may be up to code (whichever one you are looking at), but I wouldnt stake my word on it.

Just because it may or does pass inspection(s) doesnt mean it's right or up to code. I dont know of any article 725 or 800 install that would allow what you are proposing. I think day 3 of 'LV wire jockey' training was 'do not support comm cable or the like to or from electrical conduit(s)'.
 

jde75

Member
Location
Burnsville, NC
Thanks everyone for your input. I think I will err on the side of caution and tell him it needs to be run separate. I can't find anything in the NC Mechanical code specifically for this but that doesn't mean I'm not missing something. As Augie said, this will be an F2 occupancy so a little extra caution can't hurt. Thanks again :)
 