low voltage cabling

Status
Not open for further replies.

New EE

Member
Location
California
Is it permissible to run 16 awg 600 volt insulated cabling (being used for a 16 vac transformer) in the same conduit where there is 18/2 unshielded, 18/6 shielded, and CAT5e cabling in the conduit?
I wanted to provide only one conduit to go from a door that has a card reader and directory entry phone (that needs a 16 vac transformer to power it) and run all the wiring in the same conduit
from the door to the comm room but wasn't sure if I can run the 16 awg 600 volt insulated cabling in the same conduit with the other cabling per code. Thanks.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
You seem to be hung up on the fact that this is a 600v listed cable. The determining factor is that it is being used for a 16v CL2 circuit. That it has 600v insulation is irrelevant. So given that, it's installation in a conduit with other CL2 and data is just fine.

-Hal
 