srengineer1
Member
- Location
- Birmingham, Alabama USA
When calculating voltage drop for a three phase service at a distance using ACSR cable, is voltage drop calculated using motor FLA or do you need to consider motor starting current?
For standard VD calculations you use the FLA. If you are concerned aboutsrengineer1 said:When calculating voltage drop for a three phase service at a distance using ACSR cable, is voltage drop calculated using motor FLA or do you need to consider motor starting current?
srengineer1 said:When calculating voltage drop for a three phase service at a distance using ACSR cable, is voltage drop calculated using motor FLA or do you need to consider motor starting current?
eric stromberg said:if FLA voltage drop = 3%, LRA voltage drop = 18%