Low Voltage Circuit Breaker Testing

Status
Not open for further replies.

nhee2

Senior Member
Location
NH
What is the typical test frequency that others see or implement for testing of LV 480 VAC molded case breakers? In this case - 400 - 1200 A breakers with electronic trips, installed in facility switchboard. NFPA 70B (2016) recommends electrical testing every 3-5 years. What percentage of facilities do you see maintaining this schedule? Is secondary injection testing at those time intervals typical?

Thanks for any input
 
My experience is that I could get by at my facility with bi-annual maintenance, that's every other year. This was a paper and finished products manufacturing facility.
NETA MTS standard shows in Appendix B of the 2015 edition the development of a Factor for Frequency of Maintenance Tests which looks at the reliability requirement of the application and the condition of the equipment. A number is developed which is then multiplied by the Inspections and Frequency of test requirement for all the different electrical of devices and an interval is developed for testing.
I specified line injection testing for breakers that were Acceptance tested (first time), and secondary injection for the Maintenance testing with a continuity test for the CT.
 
I would think testing frequency would also depend on the environment. I worked in a die cast facility and we swapped breakers out annually and sent them out for testing at a lab.

Sent from my SM-A326U using Tapatalk
 