What is the working clearance requirements in front of a 24VDC panel?
it does not matter what it is, the same basic rules apply.Originally posted by tmacdonald:
This is for an industrial piece of equipment, does that matter? Presently, I am on site without my code book (lost to airline gremlin). Can you forward the verbage for 110.26(A)(1)(b)?
But look at this exception:110.26(A)(1)(b) Low Voltage. By special permission, smaller working spaces shall be permitted where all uninsulated parts operate at not greater than 30 volts rms, 42 volts peak, or 60 volts dc.
110.26(F) Dedicated Equipment Space. All switchboards, panelboards, distribution boards, and motor control centers shall be located in dedicated spaces and protected from damage.
Exception:Control equipment that by its very nature or because of other rules of the Code must be adjacent to or within sight of its operating machinery shall be permitted in those locations.