Gategator37

Senior Member
Does low voltage/COAX require a raceway when installed behind sheetrock in a commercial setting. From what I can remember it is, but I can't find the code reference. Thanks
 
Class 2 circuits do not require raceways or junction boxes. Article 725. Coax is covered in article 800. Pretty much doesn't need it either.

It's helpful, but not required. Also, check job specs and local amendments if they apply.
 