G Gategator37 Senior Member Dec 21, 2010 #1 Does low voltage/COAX require a raceway when installed behind sheetrock in a commercial setting. From what I can remember it is, but I can't find the code reference. Thanks
Does low voltage/COAX require a raceway when installed behind sheetrock in a commercial setting. From what I can remember it is, but I can't find the code reference. Thanks
N nhfire77 Senior Member Location NH Dec 21, 2010 #2 Class 2 circuits do not require raceways or junction boxes. Article 725. Coax is covered in article 800. Pretty much doesn't need it either. It's helpful, but not required. Also, check job specs and local amendments if they apply.
Class 2 circuits do not require raceways or junction boxes. Article 725. Coax is covered in article 800. Pretty much doesn't need it either. It's helpful, but not required. Also, check job specs and local amendments if they apply.