ymohammed00
Member
- Location
- Miami, Fl
- Occupation
- Lead LV Tech
I’m looking for the code that states a pull box is required after every two 90 degree turns. Also, what qualifies as a pull box (lb, box, etc)
You will have to determine what the Cat 6 is being used for. Is it for Remote-Control, Signaling, and Power-Limited Circuits such as Article 725 or Communication Circuits Article 800, Network-Powered Broadband Communications Systems Article 830, Premises-Powered Broadband Communications Systems Article 840 or one of the others. Then see if it refers you to one of the conduit articles which would impose the bend limit.This is for low voltage cat 6 cables. The raceway is being built currently but does not have enough pull boxes