Low voltage communication conductors in same conduit as line voltage.

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
The question has been brought up if low voltage conductors for PV communication is permitted to be installed in the same raceway as line voltage conductors? 600 volts max circuits
Your communication conductors probably should be shielded.
 

Steve16

Member
Location
Ct
Occupation
Master electrician
I run into CT wires ran through the same conduit as the service conductor "taps" a lot and cite 230.7
 

tallgirl

Senior Member
Location
Glendale, WI
Occupation
Controls Systems firmware engineer
Of course, but when in doubt, shield it.
Also, inverters make a lot of noise at frequencies which may be high enough to interfere with communication equipment. It’s not just 50/60Hz, it’s whatever the switching frequency of the inverter is.
 