hhsting
- Glen bunie, md, us
- Junior plan reviewer
Attached sketch show in electrical room following items:
1. 13.2kV 125A fused switch,
2. 2000kva 13.2kv to 480/277V transformer,
3. 3000A 480/277V switchboard,
4. 300kva 480V to 208/120V transformer,
5. 225kva 480V to 208/120V transformer
6. Low voltage less than 600V panelboards fed from swbd #3 DPR, RPB, EDMP, LPB
7. Standby generator ATS
My concern is mainly 110.26 working space and anything that relates to 13.2kV transformer
Following questions:
1. NEC 2017 110.26)A)(5) requires separation of high voltage equipment this means their has to be some separation between 13.2 kV and the 480V, 208V equipment? Correct or incorrect?
2. Is their anything in NEC 2017 section 110.26 or 450 that requires 2000KVA 13.2kV to 480/277V transformer to be in separate vault Not in same room?
3. Distances are marked on the sketch is their anything else I am missing that is not per NEC code? Clearance wise or being separate wise or anything else?