This will be a good bit for a “first“ post.
Im troubleshooting a Zurn flush valve on a urinal. When the flusher is connected to the low voltage power supply AND the urinal, it will not work.
When the flusher is disconnected from the urinal it works fine. When the flusher is connected to another urinal, the flusher works fine.
The flush valves are on their own circuit. Supply conductors are installed in EMT, EGC pulled and connected clean and text book. Transformer is mounted to a 4sq box per manufacturer instructions. Low voltage terminations are clean, in J Box. Total length of the low voltage cable is well within the allowable length.
I’ve taken the flush valve while energized and reconnected it to the urinal and I’ve watched the red LED indicator flicker and go out as I’ve tightened the nut down that attaches the flusher to the valve body.
I pulled new cable and get the same result.
the flusher has been replaced this is the second one. Same result.
i free aired the cable and have eliminated the possiblit’s of something in the wall or conduit.
I measured voltage and read 5 VDC on the valve body while the flusher is attached.
I wrapped the threads of the male connection side of the valve body with 33 to create a dielectric break and, now, the flusher will work but still read 3VDC on the valve body. Can’t leave the tape because the flusher will leak.
The chrome on the valve body and flusher both have what looks like the effects of electrolysis ( like someone wiped grease off and it left streaks) on both components.
the transformer supplying this urinal also supplies 4 other toilets and 1 urinal. Max on these toilets is 6. 1 feed off the transformer is spliced and goes 3 different directions. Only this urinal has an issue. There’s a total of 40 sensors in this building all installed the same way and this is the only place with an issue.
I think it’s a low impedance ground fault, as if the water supply to this toilet is touching something somewhere else (rebar, structural steel) and giving a shorter path to ground for the low voltage xfmr. Or a dielectric break (plastic valve installed in the cold water copper not allowing the voltage to go to ground on the cold water bond).
does anyone have any ideas how to determine what’s wrong and how to go about fixing this.
Im troubleshooting a Zurn flush valve on a urinal. When the flusher is connected to the low voltage power supply AND the urinal, it will not work.
When the flusher is disconnected from the urinal it works fine. When the flusher is connected to another urinal, the flusher works fine.
The flush valves are on their own circuit. Supply conductors are installed in EMT, EGC pulled and connected clean and text book. Transformer is mounted to a 4sq box per manufacturer instructions. Low voltage terminations are clean, in J Box. Total length of the low voltage cable is well within the allowable length.
I’ve taken the flush valve while energized and reconnected it to the urinal and I’ve watched the red LED indicator flicker and go out as I’ve tightened the nut down that attaches the flusher to the valve body.
I pulled new cable and get the same result.
the flusher has been replaced this is the second one. Same result.
i free aired the cable and have eliminated the possiblit’s of something in the wall or conduit.
I measured voltage and read 5 VDC on the valve body while the flusher is attached.
I wrapped the threads of the male connection side of the valve body with 33 to create a dielectric break and, now, the flusher will work but still read 3VDC on the valve body. Can’t leave the tape because the flusher will leak.
The chrome on the valve body and flusher both have what looks like the effects of electrolysis ( like someone wiped grease off and it left streaks) on both components.
the transformer supplying this urinal also supplies 4 other toilets and 1 urinal. Max on these toilets is 6. 1 feed off the transformer is spliced and goes 3 different directions. Only this urinal has an issue. There’s a total of 40 sensors in this building all installed the same way and this is the only place with an issue.
I think it’s a low impedance ground fault, as if the water supply to this toilet is touching something somewhere else (rebar, structural steel) and giving a shorter path to ground for the low voltage xfmr. Or a dielectric break (plastic valve installed in the cold water copper not allowing the voltage to go to ground on the cold water bond).
does anyone have any ideas how to determine what’s wrong and how to go about fixing this.