Low Voltage grounding and protection

Status
Not open for further replies.

rheimer1972

New User
Location
Ca.
Occupation
PM
Two questions. Is it anywhere in the code to put a flex connector for a phone drop down a wall at the top of the flex. Also inspector is calling us on ground pigtail in all our phone/data jacks even know it serves no purpose because they are just flexes out of the wall?
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Is it anywhere in the code to put a flex connector for a phone drop down a wall at the top of the flex.
No, but even with EMT it's common practice to protect the cable from sharp edges. For EMT and ridged they make low cost plastic push-on bushings for that purpose.

inspector is calling us on ground pigtail in all our phone/data jacks
Can't imagine that. Are you using metal boxes and he wants a pigtail in the box like you were going to use it for a regular receptacle and MC?

-Hal
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
If this is cabling on the customer side of a a PBX, then 725.3(J) would require some type of bushing.
If covered by 800 or 805, there is no requirement to protect the cables.

There is nothing in any of those articles that would require the grounding pigtail.
 

cabledawg

Member
Location
Boise, Idaho
Occupation
cable dude
As far as I know, theres no need/or code for grounding of any flex period! Especially for an outlet on the wall for low voltage! Maybe use a "P clamp to secure it to the wall up top! If rigid pipe, yes ....they make bushings for that! It might be more beneficial to buy the inspector some "hookers and cocaine"!!! lmao....joking or Am I!!!!! Peace....
 