Question from one of my classes - I want to throw out to the forum
With Cable Tray (B Line 6" Ready Rail) will have in it "low voltage" such as radio coax, Class 2 alarm cables.
Also need a power and lighting branch circuit, 120/240 volts running in the same tray.
When is a divider needed?
For example, MC cable can be run with out a divider, and no separation is required- MC cable is a chapter 3 wiring method, same with AC, NM.
But what about tray cable (Art 336) which is also a chapter 3 wiring method?
For example, a 14-2 w/ ground jacketed tray cable?
Is the divider needed with conductors and not cables? A divider would be needed with single conductor tray cable, such as 4AWG.
With Cable Tray (B Line 6" Ready Rail) will have in it "low voltage" such as radio coax, Class 2 alarm cables.
Also need a power and lighting branch circuit, 120/240 volts running in the same tray.
When is a divider needed?
For example, MC cable can be run with out a divider, and no separation is required- MC cable is a chapter 3 wiring method, same with AC, NM.
But what about tray cable (Art 336) which is also a chapter 3 wiring method?
For example, a 14-2 w/ ground jacketed tray cable?
Is the divider needed with conductors and not cables? A divider would be needed with single conductor tray cable, such as 4AWG.