Dear All,
Seeking your opinion on the below Insulation Resistance Test result for the Low Voltage cables.
Each Motor supply cables has 2runs of 3C x 120mm2 with approximate distance of 120meters.
CONCERNS:
1. Based on the IR results, are the cable acceptable to be Re-Used?
2. For motor C, what could be the reasons why it has less reading compare to other 3 motors?
Thank you in advance
Seeking your opinion on the below Insulation Resistance Test result for the Low Voltage cables.
Each Motor supply cables has 2runs of 3C x 120mm2 with approximate distance of 120meters.
CONCERNS:
1. Based on the IR results, are the cable acceptable to be Re-Used?
2. For motor C, what could be the reasons why it has less reading compare to other 3 motors?
Motor | Volt/Phase/Cycle | Phase A to Phase B | Phase A to Phase C | Phase B to Phase C | Phase A to Ground | Phase B to Ground | Phase C to Ground |
A | 460V/3/60Hz | 38.6 GΩ | 36.8 GΩ | 44.3 GΩ | 22.4 GΩ | 22.7 GΩ | 23.9 GΩ |
B | 460V/3/60Hz | 38.1 GΩ | 42.2 GΩ | 38.4 GΩ | 22.3 GΩ | 23.1 GΩ | 22.8 GΩ |
C | 460V/3/60Hz | 9.9 GΩ | 13.7 GΩ | 10.88 GΩ | 6.23 GΩ | 5.9 GΩ | 8.81 GΩ |
D | 460V/3/60Hz | 35.5 GΩ | 40.5 GΩ | 43.6 GΩ | 21.2 GΩ | 21.4 GΩ | 22.9 GΩ |
Thank you in advance