Section 300.22 limits the use of materials that would contribute smoke and products of combustion during a fire in an area that handles environmental air, and 300.22(B) provides for an effective barrier against the spread of products of combustion into the ducts or plenums.
This section applies to sheet metal ducts and other ducts and plenums specifically constructed to transport environmental air. Because equipment and devices such as luminaires and motors are not normally permitted in ducts or plenums, the wiring methods in 300.22(B) differ from those permitted in paragraph 300.22(C).
Section 300.22(C) applies to other spaces that are used to transport environmental air and are not specifically manufactured as ducts or plenums, such as the space or cavity between a structural floor or roof and a suspended (hung) ceiling. Many spaces above suspended ceilings are intended to transport return air. Some spaces are also used for supply air, but they are far less common than those used for return air.