sparkmantoo
Member
- Location
- Virginia
okay here is a good one. you have a handmade fixture. it operates at 24vdc. you have two conductors that come out of a j-box. these wires are single conductors, 24awg, looks kind of like a coaxial cable. they terminate to the fixture by means of a set screw connection. these wires are the means of support for this fixture. this fixture is pretty heavy and rather large. is this legal to (1) use the wires as a means of support, (2) use a coaxial cable to feed this fixture, (3) have a fixture that is NOT listed (homemade),and(4) is this a moot point because it is low voltage. i await everyones reply. the articles that i can reference to are 410.28(f) and 411.