I need a 480:120V, single phase, 1.5kVA transformer in a NEMA3R enclosure with lockable disconnect. So basically it is a 1.5kVA transformer with 2 primary and 1 secondary fuses in a NEMA3R box with a disconnect that can get locked out.

Anyone knows if there is an off-the-shelf solution available?

Thanks,
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I need a 480:120V, single phase, 1.5kVA transformer in a NEMA3R enclosure with lockable disconnect. So basically it is a 1.5kVA transformer with 2 primary and 1 secondary fuses in a NEMA3R box with a disconnect that can get locked out.

Anyone knows if there is an off-the-shelf solution available?

Thanks,

I don't know if they are 3R but such things are sold for control panels. call your local supply house. they are usually referred to as transformer disconnects for some reason.

here is a 500 va version. does not appear to be 3r though.

https://www.grainger.com/product/1H...4277!&ef_id=WW4KMgAAAGTwqRZY:20180416173958:s
 

Russs57

Senior Member
Location
Miami, Florida, USA
Occupation
Maintenance Engineer
You can get it special order from square d for $3500 or so.

Might want to go with fusible disconnect and separate dry transformer. Lot cheaper and quicker to get.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
All of the major suppliers have what's called a "Mini-Power Center" (Sq. D's term for it is Mini Power Zone) that is a 3R enclosed transformer that has a primary breaker and a small load center attached to it, and the breakers can have locking accessories added to them. Pre-packaged, ready to go. Smallest is 5kVA though and you have to let go of the fuse issue.

Square D

Eaton

GE

Siemens
 