Low voltage outlet hieght

Status
Not open for further replies.

jjackson1

Member
Is there a code that show low voltage outlet hieght for telephone and dat jacks? Flush mounted in wall or in syrface nonmetallic raceway
 

nakulak

Senior Member
Depending on the occupancy, there may be a minimum height required for ADA compliance, but there is no NEC required height (as far as I know)
 

JFletcher

Senior Member
Location
Williamsburg, VA
There's no NEC code, but as nakulak mentioned ADA codes (if applicable) may come into play, especially for wall mounted telephones. If this is a new commercial building, pay close attention to the blueprints, otherwise you may wind up moving a whole lotta boxes.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I generally match the power outlet height.
Exactamundo. Other reasons aside, I like to make retro-work look like it's always been there. Match height, color, finish, etc., with existing devices.

Example: when adding a switch in a room for, say, a ceiling fan, you should change the existing box, adding a gang, rather than sticking a separate box.

Of course, if you're adding more than one switch, you might use a separate box, but you'd still match existing devices and plates, and height as well.
 