Hi all,
This is regarding table 680.8 under the 2008 NEC code cycle... We have existing low voltage cables (inside conduits) that run across a new indoor pool. According to section 680.8(C), we need to follow table 680.8 for conductors operating at 0 to 750 volts to ground, to determine the clearance required above the water level. The title of that column on the table reads "Insulated Cables, 0-750 Volts to Ground, Supported on and Cabled Together with a Solidly Grounded Bare Messenger or Solidly Grounded Neutral Conductor"... if the cables are in conduit, does this section even apply?
Thanks!
This is regarding table 680.8 under the 2008 NEC code cycle... We have existing low voltage cables (inside conduits) that run across a new indoor pool. According to section 680.8(C), we need to follow table 680.8 for conductors operating at 0 to 750 volts to ground, to determine the clearance required above the water level. The title of that column on the table reads "Insulated Cables, 0-750 Volts to Ground, Supported on and Cabled Together with a Solidly Grounded Bare Messenger or Solidly Grounded Neutral Conductor"... if the cables are in conduit, does this section even apply?