Re: Low voltage path lights at pools
Thank-you for your response Ty,
Yes, we are leaning toward holding to the 10' minimum distance. And it is good to hear that there is some agreement with that. But I'm still confused. Many jurisdictions permit it. Industry claims NEC 680 allows it. ETL and UL list them.
Article 411.4 says 10' minimum, except as provided in Article 680. Well, 680 where? 680.23(A)(3)requires GFCI protection at 15 volts or more only for relamping. According to McGraw-Hill, "A GFCI is not required for low-voltage swimming pool lights (12-V units)". So, is it not required because the code section is silent on requiring it?
Lastly, and then I am taking a nap, 680.22(A)(2)states that the required isolation transformers have an ungrounded secondary, and if you could provide a GFCI on the secondary how could you do it without making the situation worse?
The best answers always make the best questions.
Thanks everyone.