Re: low voltage splice
Establishing what Article 725 is about and what it is not about. Common misconception about Article 725 is that it allows CL2 or similar "thermostat wire" or "bell wire" to be used on "low voltage" circuits.
The common bell cable that is used in residential settings and installed for door bells, is not listed per Article 725 as being classified for class 1, 2, or 3. circuits. (unless your cable is listed per Article 725) Other Articles would then Apply in this case.
90.3 This Code is divided into the introduction and nine chapters, as shown in Figure 90.3. Chapters 1, 2, 3, and 4 apply generally; Chapters 5, 6, and 7 apply to special occupancies, special equipment, or other special conditions. These latter chapters supplement or modify the general rules. Chapters 1 through 4 apply except as amended by Chapters 5, 6, and 7 for the particular conditions.
(chapter 1-4 Adds to Article 720)
720.2 Other Articles.
Installations operating at less than 50 volts, direct current or alternating current as covered in Articles 411, 551, 650, 669, 690, 725, and 760 shall not be required to comply with this article.
300.2 Limitations.
(A) Voltage. Wiring methods specified in Chapter 3 shall be used for 600 volts, nominal, or less where not specifically limited in some section of Chapter 3. They shall be permitted for over 600 volts, nominal, where specifically permitted elsewhere in this Code.
300.15 Where the wiring method is conduit, tubing, Type AC cable, Type MC cable, Type MI cable, nonmetallic-sheathed cable, or other cables, a box or conduit body complying with Article 314 shall be installed at each conductor splice point, outlet point, switch point, junction point, termination point, or pull point.
314.29 Boxes and Conduit Bodies to Be Accessible.
Boxes and conduit bodies shall be installed so that the wiring contained in them can be rendered accessible without removing any part of the building or, in underground circuits, without excavating sidewalks, paving, earth, or other substance that is to be used to establish the finished grade.
Not only a box would be required, but also have to be accessible per code.
Hope this helps.