Hello everyone,
This is the situation, I have received from a switchboard manufacturer a type test report, issued by a local authority, confirming that the switchboard is rated for 100kA. In the report are shown the internal arrangement of the busbars, structure of the switchboard, materials used, busbar sizes, etc. All seems to be OK.
Now I have requested the internal arrangement drawings specific to the project I'm running, and they look a bit different to me. They run busbars in locations not shown in the type test report, they have more breakers per sections than in the report (two vs. one in the report) and the internal spacing seems to be different dimension wise.
My question is: what are the key elements I need to look at to say that the test certificate given doesn't correspond to the switchboard being offered.
Many thanks!
This is the situation, I have received from a switchboard manufacturer a type test report, issued by a local authority, confirming that the switchboard is rated for 100kA. In the report are shown the internal arrangement of the busbars, structure of the switchboard, materials used, busbar sizes, etc. All seems to be OK.
Now I have requested the internal arrangement drawings specific to the project I'm running, and they look a bit different to me. They run busbars in locations not shown in the type test report, they have more breakers per sections than in the report (two vs. one in the report) and the internal spacing seems to be different dimension wise.