Low Voltage Systems Don't Have EGCs but ...

Status
Not open for further replies.

Stonewall

Member
NEC250 requires EGCs for all circuits regardless of voltage or if the system is grounded.

So could someone please explain to me what I'm missing.
 
Are you saying that since article 250 isn't explicitly listed as one of the "Other Articles" then article 250 doesn't apply to Class 1/2/3 installations?
 
Stonewall said:
Are you saying that since article 250 isn't explicitly listed as one of the "Other Articles" then article 250 doesn't apply to Class 1/2/3 installations?
Thats how I read it.

Where do you see this?

Stonewall said:
NEC250 requires EGCs for all circuits regardless of voltage or if the system is grounded.
 
250.4 requires an EGC for both grounded and ungrounded systems. There isn't an exemption for low voltage in 250.4 or any other section in article 250.
 
Stonewall said:
Are you saying that since article 250 isn't explicitly listed as one of the "Other Articles" then article 250 doesn't apply to Class 1/2/3 installations?

Right, that is the same reason Class 2 and 3 do not require enclosures for splices etc. But class 1 does as called out specifically in 725.25
 