low voltage termostat wiring

Merry Christmas
Status
Not open for further replies.

patl

Member
what type cabling is allowed to be used for a low voltage termostat wire to control a roof top A/C unit
 
Re: low voltage termostat wiring

If the cable is passing through a plenum ceiling, make sure the cable is plenum rated. (cmp)
 
Re: low voltage termostat wiring

JohnJ: chances are this is not a plenum space but air handling space. A plenum is inside a duct. The area above a suspended ceiling may be used for return air, or not.
See table 725.61 for cable types and substitutions are shown in Figure 725.71. CL2 may not be the correct cable.

[ March 11, 2004, 09:17 PM: Message edited by: tom baker ]
 
Re: low voltage termostat wiring

guy thanks for your responces, I now think I know what to use now, I left out the fact that I will be passing through floors that being said I believe I will need CL2R. Is that correct?
 
Status
Not open for further replies.
Top