Hello,
I am being told by an inspector if a low voltage lighting fixture in a store has a Class 2 transformer it must be hardwired.
Also that It must be placed in a metal enclosure, which I do not see in UL-962 & UL-65.
Typically we don't hardwire the LED lights and the transformer and we never use a metal enclosure for the transformers. We use UL-Listed Transformer without a metal enclosure which comes with a plug that directly plugs into the wall.
Could it be because this specific transformer is located in a metal enclosure and the plug is hardwired inside the metal enclosure?
Inspector is suggesting to remove the plug and attach a metal conduit which must be hardwired by an electrician at the store. I am trying to understand that why does a low voltage transformer require a metal enclosure and why is a metal conduit required for the cord plugging into the low voltage transformer. I understand if it was a quadbox or a jbox or a combination of the two but it is just a class 2 transformer rated less than 100W..
I tried to look up the code for Michigan to see if it any different but I am can't find any related information..
Can you some one please advise?
I am being told by an inspector if a low voltage lighting fixture in a store has a Class 2 transformer it must be hardwired.
Also that It must be placed in a metal enclosure, which I do not see in UL-962 & UL-65.
Typically we don't hardwire the LED lights and the transformer and we never use a metal enclosure for the transformers. We use UL-Listed Transformer without a metal enclosure which comes with a plug that directly plugs into the wall.
Could it be because this specific transformer is located in a metal enclosure and the plug is hardwired inside the metal enclosure?
Inspector is suggesting to remove the plug and attach a metal conduit which must be hardwired by an electrician at the store. I am trying to understand that why does a low voltage transformer require a metal enclosure and why is a metal conduit required for the cord plugging into the low voltage transformer. I understand if it was a quadbox or a jbox or a combination of the two but it is just a class 2 transformer rated less than 100W..
I tried to look up the code for Michigan to see if it any different but I am can't find any related information..
Can you some one please advise?