We have been asked to install a silent alarm system in an office area. The alarm will consist of a series of strobe lights that operate on 6 volts DC. These lights will be ceiling mounted to a suspended ceiling throughout the space. Is it permissible to make open low voltage splices in a plenum ceiling, or do the splices need to be enclosed in a box? We will be using plenum rated cable.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Should be fine.

-Hal

Just be careful if you are splicing at the device. Many devices, in fact all strobes that I'm familiar with, are required by the manufacturer to be mounted to a box. The box will then have to be properly supported.
 