I was doing a side job for a friend and amongst other things he showed me a low voltage transformer with wires already ran and working some existing lights.....there was a single wire not connected to anything and he wants me to connect it and get it working....i have not worked on very many lo-vo xfmrs and was wondering if anyone can help me out.....it was 18 awg wire...looked alot like lamp cord with the two split sides.....i dont know if one side was ribbed or not as i did not touch it or spend much time looking at it (i had a list of other things to do and that was thrown in at the end)
http://www.technomagnet.com/mt-1200.htm
this is the link to the xfmr......to see the specs you need a PDF reader.....i can send a link for that as well if needed
Thanks in advance
For starters, Low voltage wiring is not much different from the higher voltage we use in buildings, but remember ohms law, this will produce much higher current levels, and resistance of a circuit can be a problem on long runs, which will cause bad voltage drop problems, never use a listed outdoor transformer, or circuits from one to feed indoors, or visa versa.
18awg seems way two small for this transformer, as it shows the smallest conductor to it as a 14awg. this transformer has two transformer cores, each core has two protected outputs, these are likely a auto reseting circuit breaker, at about 25-30 amps.
Three things to keep in mind when sizing the wire is, how many lamps can be on each circuit (300 watts total each circuit, 1200 total with this transformer), wire size, and voltage drop. I run a ring circuit sometimes to over come the voltage drop that leaves the lights at the end of the run looking dim, by running through the circuit alternating every other light, then back picking up the ones I left out, then back to the transformer making sure of the correct polarity this places each light at the same voltage drop in the circuit so they will all have the same brightness.
But as to your original question. First, in these applications polarity is not an issue since it is an AC circuit and a resistive load (incandescent lamps), but can be a factor in a ring circuit.
As to where to put the lonely wire? you have to have two conductors to make a circuit, one wire wont do it, so I would say you need to find the other wire that will complete the circuit and make sure one is attached to the common, and one is connected to one of the taps on that section of the transformer, always use the lowest tap voltage like the 12 volt one first, then check the voltage at about the middle of the whole circuit, then select to correct tap to bring the average voltage back to the 12 volts needed at the lights, if this is a single run you will have a higher voltage reading at the closest lights to the transformer and have lower reading the farther you get from the transformer.
Hope this helps:wink:
That does help......i mis-worded some stuff in the OP......it is not a single wire....but a 2 conductor flat cable.....it probably is 14awg......it was one of those things that we walked past and he said "Oh yeah....I need this wire hooked up eventually too"....to which i replied "i'm sure i can figure it out" and really didn't get to involved the day i was there as i knew i had to go back for other things he wanted done and that was not on my list for the day
I do believe you answered my question though.....i was wondering if it needed to be connected 1 hot and 1 neutral....but you telling me it is an AC circuit is what i was wondering...thanks for that
the lamps are mr-16 and there is only 4 lights about 15 feet from the xfmr....i think that should be fine
These low voltage (landscape) type lighting transformers are isolated output and don't have any bond or reference to earth or the line side ground, so that is why the polarity isn't as important as it is in building wiring where we must observe polarity.
With that short of run just use the common and the 12 volt tap of an un used section, and you should be fine.
Glad to be of help;)