That's true for constant power, i.e., I = P/V. For constant resistance I = V/R, so not in that case.I always thought the lower the Volts, the higher the Amps. I found out that that's not always the case. So my question is when is it the case, and when is it not the case. Thank you for your help.
There's a good graph that gets posted occasionally that has motor amps at varying voltages. Maybe someone can find it and post itAn assumption most often made is that since low voltage increases the amp draw on motors, then high voltage must reduce the amp draw of the motor.
That’s not entirely true.
Higher voltages than expected on a motor will push the magnetic portion of the motor into saturation. This causes the motor to draw excessive current in an effort to magnetize the iron past the point that magnetizing is practical.
So short answer.. it depends
There are also the tables right out of the NEC for example 430.248 or 430.250.There's a good graph that gets posted occasionally that has motor amps at varying voltages. Maybe someone can find it and post it
Resistive loads like a heater lower the voltage lower the current (directly proportional) . Inductive loads like a motor lower the voltage increase the current (inversely proportional).
To add: Yes, that's what the math says when you get to choose which values are the constants and which values are the variables.I always thought the lower the Volts, the higher the Amps.
Like so many other rules of thumb, this is applicable only in a few specific circumstances when several specific criteria are met.I always thought the lower the Volts, the higher the Amps. ...
Isn't that what I said in post #3?Don't get confused by the difference between applying a different voltage to a given piece of equipment
. . . and . . .
Equipment designed to produce (or use) a given amount of power when supplied by a different voltage.
It's true when the equipment is built to match the voltage. When talking about delivering a given power, the P = E x I math applies. To deliver a given power, current varies inversely with voltage. Also, loads like motors use less current when the voltage increases (within its design voltage range).
When talking about applying a different voltage to equipment with no change to the equipment, then the I = E / R Ohm's Law math applies. The current varies proportionately with applied voltage. This describes most electrical loads which behave as resistive loads do. If the voltage increases, so does the current.
The lower the current is not always the lower the amps. We regularly have higher current with lower current or higher versa. Paper mills can operate either way.
To us who understand it, yes. To someone who needs to ask, maybe not.Isn't that what I said in post #3?![]()
Interesting that according to that graph, the common premise of the volts/amps inverse relationship is not really true. It's more true for when voltage goes down but not really for when voltage rises. Another interesting thing to note is that when voltage rises beyond a few percent, amperage also rises, but the power factor is decreasing so it's (roughly) still constant power.Here it is without the accompanying white paper.
Lower the Volts, higher the Amps, and vice versa does not necessarily mean that the higher the amps. The amps can be higher or lower.