Regarding feeders, can someone explain the difference between life safety and emergency? How would one identify life safety feeders from emergency feeders? Thanks.
Regarding feeders, can someone explain the difference between life safety and emergency? How would one identify life safety feeders from emergency feeders? Thanks.
I'm guessing that his question is regarding NEC Chapter 7.
Then the term Life Safety is not correct, it is only used in article 517 as far as being a specific system.
Roger
I agree but knowing where mstrlucky works fire alarm and egress lighting are often (incorrectly) called life safety. Maybe he can clarify if this is actually an Article 517 installation.
Power riser says all EM feeders are to be MI cable. That to me is incorrect. All EM feeders are never MI, just usually fire pump and genset.
Sounds like a waste of someones money. Just to clarify these are part of the Article 700 emergency system? There is no Article 701 Legally Required Standby in the NYC electrical code those requirements fall under Article 700.
I don't follow what your asking. How would I know what your referring to?
If you go back to post #2 you'll see that true "life safety" falls under Article 517, are you talking about a health care facility?
Yes.
OK then Roger was correct. :ashamed1:
Bid it and install it per the bid documents including specs.
Roger