I am the process engineer of a remote plant. The site is large and serviced by a 25kv 3 phase private power line that we own. The service at the utility is a 600v 400A with step up transformer bank. Since the site is very large and the loads far appart, there are 200 A 600v service drops where needed. We were sold the idea that LSIG breakers on each main service could make the workplace very very safe by allowing any fault to be cleared by this device before causing any harm. Expect ally to the workers.
We don’t mind if whatever is on this service goes off in case of a fault. We don’t mind having to search what was the problem instead of having bangs and smoke. Most of the loads are pumps motors. With the largests being 75hp.
The first breaker was installed years ago and always performed as intended. Fuses would not burn but the breaker would trip. We recently had a line to line fault that created burns and smoke and burnt load fuses. Not used to this. I suspect that all the faults we encountered before were line-ground and the device handled this as planned, but the recent one was line-line and the settings are not as good for this type of faults.
I am not an electrical engineer but I understand most of the concepts, and when I talk to local specialists, they talk about the necessary coordination of the protections. It’s not that practical as a concept to apply with step up/step down and overhead power line protections that creates 40A on 600v for each 1A increment on 25kv, while the current on the primary is less than 10A…
My aim would be to set the LSIG as sensitive as possible to allow motor inrush current and nothing more. This would likely lead to the LSIG breakers clearing faults before the fuses pick up. I don’t care about this but apparently the code cares.
Any suggestions?
We don’t mind if whatever is on this service goes off in case of a fault. We don’t mind having to search what was the problem instead of having bangs and smoke. Most of the loads are pumps motors. With the largests being 75hp.
The first breaker was installed years ago and always performed as intended. Fuses would not burn but the breaker would trip. We recently had a line to line fault that created burns and smoke and burnt load fuses. Not used to this. I suspect that all the faults we encountered before were line-ground and the device handled this as planned, but the recent one was line-line and the settings are not as good for this type of faults.
I am not an electrical engineer but I understand most of the concepts, and when I talk to local specialists, they talk about the necessary coordination of the protections. It’s not that practical as a concept to apply with step up/step down and overhead power line protections that creates 40A on 600v for each 1A increment on 25kv, while the current on the primary is less than 10A…
My aim would be to set the LSIG as sensitive as possible to allow motor inrush current and nothing more. This would likely lead to the LSIG breakers clearing faults before the fuses pick up. I don’t care about this but apparently the code cares.
Any suggestions?