I was looking at some of our newer Allen Bradley thermal mag breakers, and saw adjustable dip switches for L, S, I, and G. In my mind you adjust L for the motor's full load amps (not exact, but close), S for the motor's inrush, I for the instantaneous trip, and G for the ground fault current.
However, I saw another dip switch that said %N, and you could adjust it for On or Off, and for 0%, 50%, or 100%. Has anyone encountered this setting before? Thanks
I think you are a bit confused about what you have and what you are using it for.
LSIG would imply this is an ELECTRONIC Trip Unit (ETU) circuit breaker, NOT a "Thermal-Mag" circuit breaker.
L = Long Time trip, the equivalent of the "thermal" in a Thermal-Mag breaker.
S = Short Time trip, no equivalent in a T-M breaker, used for coordinating with other breakers up and down stream
I = Instantaneous trip, the same as a magnetic trip in a T-M breaker
G = Ground trip, again, no equivalent in a basic T-M breaker and if GF is added to one, it's generally a separate module.
%N = Neutral current, you would only see that adjustment on a 4 pole breaker, not commonly used in North America, but the %N = the neutral current as a % of the L current in that 4th pole that you want it to trip on.
Then you go on to mention Motor FLA? You don't use ETUs of a circuit breaker to protect a motor directly, it is branch or feeder circuit protection. There ARE versions of these breakers referred to as "Motor Protection Circuit Breakers" (MPCBs) that have adjustable thermal trips and are listed as "Manual Motor Starters" for that purpose, but they will not have LSIG (or N) trip settings, so if you have those settings, it is not an MPCB. If you want an MPCB, you have to buy an MPCB, different part number.
So what is it you plan on doing with this breaker? If you have a part number on the breaker, that would be helpful in that endeavor.