mako

Member
Sir,

Is it approved to directly connect a Liquid-Tight
Flxible Metal Conduit at the end of a given conduit, say EMT,PVC,RSC or IMC with an approved fitting or through an intermediary juction box first?The lenght of the flexible is around .5 meter( 20 inches).

Thanks.
 
Re: LTFMC

It would be approved by my jurisdiction to make a direct transition between two raceway types. Just make sure you have an appropriate egc if the raceway you are connected to is serving as the egc means.
 
Re: LTFMC

As I sidenote, I would never use LTFMC under any circumstances. I have seen several cases where the internal metal spiral was completely destroyed by corrosion.
 