Nardie
Member
- Location
- North Augusta, SC USA
I need some advice on this, I have a new load bank rated at 451A. From the breaker to the load bank the vendor installed parallel #3/0 AWG conductors. Based on NEC table 310.16 at 90 degree C the cables are rated for 225A, in parallel this would be 450A. This is my first problem since 451A from the load bank exceeds the rating for the #3/0 AWG conductors. If I follow NEC article 110.14(C) the ampacity of the conductors should be sized for 75 degree C. Per this article the ampacity of the #3/0 AWG conductors are only 200A, in parallel this would be 400A. So my design organization is recommended replacing the #3/0 AWG conductors with #4/0 AWG conductors. At 75 degree C the #4/0 AWG parallel conductors would be rated at 460A. So, the design organization is recommending the LTPU breaker setting to be at 455A. I believe this is set to low since the FLA for the load bank is 451A. I plan to test the load bank for at least 4 hours at full load and I'm worried about nuisance tripping of the load bank breaker during this test, since the LTPU setting is so close. Is there something in the NEC that would allow me to set the LTPU breaker setting at the 90 degree C rating of 260A for #4/0 AWG conductors, in parallel 520A, or am I misunderstanding article 110.14(C)? Any help would be appreciated, thanks in advanced.